tswiczko
Thread starter- Joined
- Feb 15, 2009
- 838
Got a question I had been a service tech for about 15 years. my S.I.L. asked me to look at her A/C the other day because she has someone coming to replace the compressor. He says it's worn out.
complaint is, It does not keep up and runs constantly.
I don't think it is the compressor. What do you guys think?
installed 1993
2.5 ton
fixed orifice
both coils are clean and in good shape
amp 6.5 of 9 fla
head 200psi. out door temp87*f
suction 100psi.
in door temp 77*f
temp split across the coil 13*f
super heat is 8*f
when I pulled my low side manifold line off, there was liquid (mist) not oil.
compressor sounds quiet,(not rattly) and sweating on can
no one has put any refrigerant in it to cause an overcharge.
I suspect the piston is stuck or the seal on the end of the piston is damaged.
causing the flooding back and causing the low head and high suction and flooding back.
it has been my eaxperience that a worn out compressor causes a higher than normal amp draw and doesn't cause flooding back.
installed 1993
2.5 ton
fixed orifice
amp 6.5 of 9 fla
suction 100psi.
in door temp 77*f
super heat is 8*f