What size of pipe should I use to run 5, #8 wires in. I was thinking that 1 inch would work, but might be a little tuff to pull the 100ft run.
 

sangerwaker

Commander
Joined
Jul 29, 2004
Messages
2,059
Re: electrical question

1" is barely big enough per NEC. It really depends on the type of wire (THHN, XHHW, etc) and the type of pipe (EMT, PVC Schedule 40 or 80, or flexible metal conduit, etc). Use 1-1/4" minimum. It will pull easier if you go even larger, say 1-1/2".<br /><br />EDIT-also make sure you use a good quality pulling lube. It will make it MUCH easier.
 

vipzach

Lieutenant
Joined
Feb 15, 2005
Messages
1,283
Re: electrical question

It will be EMT pipe and the wire is THHN. I was pretty sure that the 1" was legally big enough, but I am just afraid that it will be a tuff push through the pipe. Thanks for saying something about the pulling lube. That will help!
 

Bob_VT

Moderator & Unofficial iBoats Historian
Staff member
Joined
May 19, 2001
Messages
26,064
Re: electrical question

I ran over 200 feet of 3 conductor wire through a piece of flexible black pvc water pipe. I used a mouse and blew it through the pipe with a string attached.... then a cable .... then the wires. Alot of work but we did not use any lubricant (lol it would have helped).
 

Kenneth Brown

Captain
Joined
Feb 3, 2003
Messages
3,481
Re: electrical question

Don't push it through. Tie a good strong string(100 line like you use for trot line) onto a plastic bag from the grocery store. Put it into one end of the pipe. Attatch a wet/dry vac to the other end. It'll suck the string through. Tie the string to the wire and pull it through.
 

Kenneth Brown

Captain
Joined
Feb 3, 2003
Messages
3,481
Re: electrical question

Just so Bob doesn't think I stole his idea notice we posted at the same time. ;)
 

sangerwaker

Commander
Joined
Jul 29, 2004
Messages
2,059
Re: electrical question

Fill chart says max of 9 8AWG THHN type wires in a 1" EMT. Prolly wouldn't be too bad of a pull. Lube will help. How many 90's and 45's in the pull?
 

vipzach

Lieutenant
Joined
Feb 15, 2005
Messages
1,283
Re: electrical question

There will be six 90's. They just called and told me they bought 1" EMT. I am going to just lay the wire out and pull to each 90.
 

heyttown

Chief Petty Officer
Joined
Aug 3, 2003
Messages
537
Re: electrical question

with 6-90's I hope you have a pull point installed somewhere along the line....Max degree in conduit bends allowed per code from 1 pull point to another is 360 degrees...<br /><br />1 junction box somewhere in there after the 2nd or 3rd 90 should do the trick.
 

vipzach

Lieutenant
Joined
Feb 15, 2005
Messages
1,283
Re: electrical question

Thanks heyttown, I will put one in there tonight, when I start running the pipe. Thanks for your help guys.
 

vipzach

Lieutenant
Joined
Feb 15, 2005
Messages
1,283
Re: electrical question

Originally posted by crab bait:<br /> stranded is much easier pull then soild wire,,by far..
I agree, we already bought stranded. :D
 

fireship1

Chief Petty Officer
Joined
Aug 26, 2003
Messages
581
Re: electrical question

Make sure that you use actual "pulling lube" for electrical cable. Soap or grease will degrade the insulation of the cables. :eek:
 