Originally posted by divo:<br />
Originally posted by stl:<br /> It is in a metal box, but there was not metal conduit. The original wire just had a hot and neutral, with no ground. With the new wire I attatched the hot to the hot and the neutral to the neutral. This junction just so happened to be a half inch from the main water line so i attatched the new ground to the water line. If this is really that unsafe I will take it down, and think of something else. I thought this would be better than having an open ground, or running a two prong outlet with no ground.
Turn Light on, Take a volt meter and put one lead on the metal box ( make sure contact with metal), then take the lightbulb out and CAREFULLY touch the other lead to the center tab in the lamp socket without contacting the threads. If there is 120v there, connect ground wire to box. If no voltage, take lead off center tab and touch to the threads the bulb screws into. If it reads 120v, the fixture is reverse wired. Flop the wires on the fixture and connect ground to box. If no voltage in either test, the box isnt grounded. To do properly, and avoid any hassles in the future, this should be fixed. IMO this would be a inexpensive and easy fix that should be done.