Buying a generator for house.What should I expect to pay an electrican?

crazy charlie

Vice Admiral
Joined
May 22, 2003
Messages
5,602
Will be picking up a generator for emergencies.Hope to never use it.What should I expect it to cost me to get a hookup to my fuse panel .Adapter to plug into gen ,not an automatic setup.Simple works for me.Thanks Charlie
 

rbh

Fleet Admiral
Joined
Mar 21, 2009
Messages
7,939
Re: Buying a generator for house.What should I expect to pay an electrican?

Not sure the rates you pay electricians in your town.

I have an old onan 4.0 CCK 3 phase that I will hook up for the shop/well house, I know I need to have a switch installed that isolates the grid power from the generators power so I don't fry the line guys by back feeding power down the line.

How many watts does your genset put out? enough to run all the appliances in your home? You may want another switch installed to isolate certain runs, electric water heater, base boards, ETC

And you should probably have a pad/mounting area away from your home because of the exhaust and sound
 

crazy charlie

Vice Admiral
Joined
May 22, 2003
Messages
5,602
Re: Buying a generator for house.What should I expect to pay an electrican?

Wow,that looks easy !! With my luck PSEG wont get involved with something like that.Thanks Charlie
 

roscoe

Supreme Mariner
Joined
Oct 30, 2002
Messages
21,770
Re: Buying a generator for house.What should I expect to pay an electrican?

That does look good !

I have a 6k portable, But have only needed to use it a few times in 14 years.
Up till now, I simply ran a gfi extension cord into the house.
Good for the furnace, fridge, a lamp, and the incubator when I have eggs in it.


Gonna check out the generlink for sure. Would be great, in the event the power was out for more than a few hours.

Cost seems to range from $500 to $950, depending on the local utility.

Hmmm, how will I know when the power comes back on?


Thanks for the tip.
 
Last edited:

Grandad

Lieutenant Commander
Joined
Jun 7, 2011
Messages
1,504
Re: Buying a generator for house.What should I expect to pay an electrican?

You might also consider a natural gas powered generator, if you have NG available. You could manage without utility power indefinitely.
- Grandad
 

sam60

Captain
Joined
May 21, 2011
Messages
3,189
Re: Buying a generator for house.What should I expect to pay an electrican?

Hi Charlie. I'm an electrician, but I think that this set up would be the bees knees. Simple, safe, flexible and easy to understand. No electrician required. Check with your utility to see if they have such a program. - Grandad
http://www.google.ca/url?sa=t&rct=j...dXFVbLCRfeoxlXyww&sig2=hkREaf4Jpeq2-YSprqTD1A

That is very nice, I've been looking at a setup that is a lot more expensive....this makes more sense ($) than what I was thinking of doing.

GE 13,000-Watt Standby Generator System with Symphony II Whole House 200-Amp Automatic Transfer Switch-40324HD at The Home Depot
 

Scott Danforth

Grumpy Vintage Moderator still playing with boats
Staff member
Joined
Jul 23, 2011
Messages
50,604
Re: Buying a generator for house.What should I expect to pay an electrican?

Since I use a portable genny and do not have an automatic switch gear, here is what I do

I have a 50 amp outlet for my welder. I use the same outlet to connect my generator to. I kill the main breaker, kill the water heater breaker, kill the pool breaker and use a 6600 watt (8k starting) genset for when power is out. if I had a 10k gen, I could leave the hot water heater breaker.

I am currently looking for a used 10k genny at the local pawn shops. My hopes is it sat with fuel in the carb and I can get one dirt cheap because it wont start.
 

bigdee

Commander
Joined
Jul 27, 2006
Messages
2,667
Re: Buying a generator for house.What should I expect to pay an electrican?

Since I use a portable genny and do not have an automatic switch gear, here is what I do

I have a 50 amp outlet for my welder. I use the same outlet to connect my generator to. I kill the main breaker, kill the water heater breaker, kill the pool breaker and use a 6600 watt (8k starting) genset for when power is out. if I had a 10k gen, I could leave the hot water heater breaker.

I am currently looking for a used 10k genny at the local pawn shops. My hopes is it sat with fuel in the carb and I can get one dirt cheap because it wont start.

Yeah that is what I do too....BUT that is not the smartest way to do it. It is not fail safe, trip the main and you could fry a lineman. When I was younger I was not worried about it but now I am afraid that I might slip up and accidentally throw the main. This forum has got me thinking....I will be ordering a double pole/double throw switch and do it the safe way.
 

lckstckn2smknbrls

Lieutenant Junior Grade
Joined
Sep 18, 2008
Messages
1,114
Re: Buying a generator for house.What should I expect to pay an electrican?

You might also consider a natural gas powered generator, if you have NG available. You could manage without utility power indefinitely.
- Grandad
This is what my parents have. They travel a lot and don't have to worry about anything back at the house.
 

MikDee

Banned
Joined
Jun 6, 2007
Messages
4,745
Re: Buying a generator for house.What should I expect to pay an electrican?

Grandad still has parents!? :eek:

By the way, important subject, thanks for the info!;)
 

Bayou Dave

Lieutenant Commander
Joined
Dec 13, 2012
Messages
1,780
Re: Buying a generator for house.What should I expect to pay an electrican?

Since I use a portable genny and do not have an automatic switch gear, here is what I do

I have a 50 amp outlet for my welder. I use the same outlet to connect my generator to. I kill the main breaker, kill the water heater breaker, kill the pool breaker and use a 6600 watt (8k starting) genset for when power is out. if I had a 10k gen, I could leave the hot water heater breaker.
I am currently looking for a used 10k genny at the local pawn shops. My hopes is it sat with fuel in the carb and I can get one dirt cheap because it wont start.

Here you go. Lots of generators:
White Owl - Generators
 

pnwboat

Rear Admiral
Joined
Oct 8, 2007
Messages
4,251
Re: Buying a generator for house.What should I expect to pay an electrican?

Scott Danforth's Avatar

Join Date
Jul 2011
Location
Manitowoc WI / Bradenton FL
Posts
4,298

Default Re: Buying a generator for house.What should I expect to pay an electrican?

Since I use a portable genny and do not have an automatic switch gear, here is what I do

I have a 50 amp outlet for my welder. I use the same outlet to connect my generator to. I kill the main breaker, kill the water heater breaker, kill the pool breaker and use a 6600 watt (8k starting) genset for when power is out. if I had a 10k gen, I could leave the hot water heater breaker.

I am currently looking for a used 10k genny at the local pawn shops. My hopes is it sat with fuel in the carb and I can get one dirt cheap because it wont start.
My parents had a similar set up but it ran off of propane gas.
 

wrench 3

Commander
Joined
Aug 12, 2012
Messages
2,108
Re: Buying a generator for house.What should I expect to pay an electrican?

I figured that we only need emergency power so I ran two lines into the house and put one outlet by the well pump and one by the fridge. If the power goes out I change the plugs from there regular receptacle to the ones hooked to the generator. Our back up heat is wood, so we can get by without the heaters, and any thing else (electric kettle, microwave, etc.) can be plugged into the spare half of one of the duplex receptacles from the generator.
 

joed

Lieutenant Junior Grade
Joined
Sep 28, 2002
Messages
1,135
Re: Buying a generator for house.What should I expect to pay an electrican?

Since I use a portable genny and do not have an automatic switch gear, here is what I do

I have a 50 amp outlet for my welder. I use the same outlet to connect my generator to. I kill the main breaker, kill the water heater breaker, kill the pool breaker and use a 6600 watt (8k starting) genset for when power is out. if I had a 10k gen, I could leave the hot water heater breaker.

I am currently looking for a used 10k genny at the local pawn shops. My hopes is it sat with fuel in the carb and I can get one dirt cheap because it wont start.

That is totally not to code. Along with the fact that most welders don't have a neutral. You must have a system that is fail safe. It has to be impossible for the generator and the main breaker to be on at the same time. There are interlock kits available for breaker panels that make it impossible for the generator breaker to be on unless the main breaker is off.

Also the fact that you need a suicide cord (cord with two male ends)to connect the generator is dangerous. If you unplug either end with the power on you have live prongs sticking out.
Here is a picture of one model.

Generator_I_K.gif
 
Last edited:

agallant80

Commander
Joined
Oct 25, 2010
Messages
2,328
Re: Buying a generator for house.What should I expect to pay an electrican?

Im not sure if I will get blasted for this or not but I have my 2200w generator. I made an extension cord that is male on both ends. I plug it in to the outlet on the side of my house. Before I do this I turn off all of the breakers under my meter. My Fridge, stove, water heater and heat pump will not work just one side of the subpannel in my house which is enough for the bathroom, living room and bedroom.
 

JustJason

Vice Admiral
Joined
Aug 27, 2007
Messages
5,323
Re: Buying a generator for house.What should I expect to pay an electrican?

You should expect to pay 100 to 120/hr for a good electrician. Everything after that is parts. And nobody is going to know whats needed until they sketch out the installation.
 

bigdee

Commander
Joined
Jul 27, 2006
Messages
2,667
Re: Buying a generator for house.What should I expect to pay an electrican?

Im not sure if I will get blasted for this or not but I have my 2200w generator. I made an extension cord that is male on both ends. I plug it in to the outlet on the side of my house. Before I do this I turn off all of the breakers under my meter. My Fridge, stove, water heater and heat pump will not work just one side of the subpannel in my house which is enough for the bathroom, living room and bedroom.

I think there are a bunch of us that are guilty of this. Now that I am retired and bored half the time I may put a DPDT transfer disconnect on mine. They are fairly inexpensive.
 

agallant80

Commander
Joined
Oct 25, 2010
Messages
2,328
Re: Buying a generator for house.What should I expect to pay an electrican?

I think there are a bunch of us that are guilty of this. Now that I am retired and bored half the time I may put a DPDT transfer disconnect on mine. They are fairly inexpensive.

I live in a "historic" part of town with old trees and above ground power. We will loose power once a year for at least 24 hours and several times a year for 3+ hours. Its nice having electricity.
 

hungupthespikes

Master Chief Petty Officer
Joined
Sep 25, 2009
Messages
814
Re: Buying a generator for house.What should I expect to pay an electrican?

Im not sure if I will get blasted for this or not but I have my 2200w generator. I made an extension cord that is male on both ends. I plug it in to the outlet on the side of my house. Before I do this I turn off all of the breakers under my meter. My Fridge, stove, water heater and heat pump will not work just one side of the subpannel in my house which is enough for the bathroom, living room and bedroom.

You could have a serious problem if your back feeding 20amps (2200w) thru a 15 amp breaker/14 gauge wire in the house. Yea the breaker should protect the wire, but the breaker is not designed to protect when it's being feed from the wrong side. It's to protect the wire down line (beyond the breaker, not up the line, power coming in. The 20-25 amp breaker on the gen is for that, and your house wire/receptacle may not be sized right. :mad2: :flame:

Just so we all know. Back feeding is very dangerous and illegal. If it does get out of you house, older transformers do work both ways. 220 in the low end will come out the top at the higher voltage and will go right on down the line to the poor lineman. :facepalm:

rant over