Re: Carrier A/C, Again!
The numbers are:
Outside temp 100.4
Suc temp 66.2 (under the line insulation)/71.6 (on the expose line)
Liqu temp 107.6
Fan temp 116.6
Suc PSI 77
Liqu PSI 300
Register temp 64.4
Return temp 77, Which is also the average temp at the house. I have set the thermostat to 74 deg.
The neighbors system which is the same of what I have and still stock system looks as follow:
suc temp 57.2 (under the line insulation)
liqu temp 109
fan temp 114.8
I did not dare hook to her system to check the psi and have no access to the inside. Just thought I gave those numbers to compare. Her house is also smaller and the load in the system is .4 lbs less than mine so I dont think there is much difference to worry about. Her outside unit is also in the shadow where mines is under the sun all the time, not sure that will make a lot of difference, I will think not...
I will check into that valve later but I noticed it is a 3.5+ ton system so that exact one would not fit. Any other part numbers will be welcome. If I find anything else I will post it here...
Thanks everyone!
UPDATE: I saw the Danfoss tr6 - 067l5857 which is 2.5 - 3 ton. I should had looked more... I called the shop but it seems they are gone. Will try again tomorrow... Would I be wrong in assuming that if this TXV is still not large enough after adjusting I can anyway ad that manual valve right? Will adding the manual valve to the original non-adjustable valve be an option?
As far as brazing the parts in and the copper flaking, what are the alternatives?