I have two 14 ga 15 amp circuits in my detached garage.
The 2 circuits come from opposite sides of my panel, so there is 240V out there.
I wired up an outlet for my Lincoln MigPak 180 welder from hot to hot off each supply. It works fine. It requires 20A peak according to its specs, but has never popped a 15A breaker.
I would like to plug a 4800W construction heater into it...was going to lop off the heater's plug and just put the same type as on the welder..... it should pull 20A at 240V.... think it'll pop the 15A breaker?
before I waste $80 on the heater.... I suppose it could be turned down too...I haven't looked closely at those heaters....
A 3500 watt heater would be nice, but they all seem to be 4800W
The 2 circuits come from opposite sides of my panel, so there is 240V out there.
I wired up an outlet for my Lincoln MigPak 180 welder from hot to hot off each supply. It works fine. It requires 20A peak according to its specs, but has never popped a 15A breaker.
I would like to plug a 4800W construction heater into it...was going to lop off the heater's plug and just put the same type as on the welder..... it should pull 20A at 240V.... think it'll pop the 15A breaker?
before I waste $80 on the heater.... I suppose it could be turned down too...I haven't looked closely at those heaters....
A 3500 watt heater would be nice, but they all seem to be 4800W